A couple of points that might (?)_ be helpful: A regulator made for CO2 usually will be capable of high side gas pressures of 2000 or even 3000 psi. CO2 tanks are usually specified for around 1800 psi, or 2000 psi, or more depending under whcih DOT regulation specification it was certified. A CO2 tank in the USA is allowed under DOT regulations to be filled to a specified weight (which is actually stamped on the tank along with the Tare weight). Contact me offline if you wnat to know how to translate what's stamped on the tank. The DOT specified net weight that a CO2 tank can hold results in a tank pressure at normal room temps of about 650-850 psi. If the gas shop overfilled your CO2 tank enough to break a CO2 regulator, they must be ignoring the DOT regs and your safety as well since they would probably have to be filling the tank to more than 2000 psi. If that's the case, consider finding another gas shop. Diff regulators will be designed for diff optimum operating low-side pressures. I have a Scott's 2-stage regulator that's stable down to just a few PSI. But it's a very expensive regulator (about $400 new) that I picked up used just to try it. Some regulators have an optimum low side range above 10 psi. I think most of the CO2 regulators for the hobbyists are good down to about 10 psi. I can find your model in the Victor price list but not the specs -- but I suspect the regulator can withstand high side operating pressures of at least 2000 and probably 3000 psi. ***** Adjusting regulator outlet pressure. Unless the outlet line is partly open then adjusting the regulator to a lower outlet pressure will not show results on the low side pressure gauge. The pressure can't drop until some of the gas in the low side of the system leaves. One way to see fast results is to adjust the regulator lower and then open the metering valve until the regulator low side gauge stops lowering. The same problem doesn't occur for adjsuting the regulator higher -- in that case, more gas is forced into the low side until the set pressure is reached. ***** I'm not familiar with NoShok's line of needle valves or find any cv specs on their website, so I can't comment on their performance. Generally, diff valves will be usefull for diff ranges of gas flow and for aquatic gardening, we're interested in very tiny rates of flow. The lower the volume of gas flow for which a valve is intended, the more likely that it will be easy to make subtle adjustments. The others, intended for large flow rates, will change the aquatic gardener's CO2 flow tremendously if one just barely turns the knob at at all. That's an inconvenience and not a fatal flaw. I prefer the expensive Swagelok B-SS4, which allows one to make large turns of the knob for very small changes in gas flow -- but most folks are content with cheaper valves. *************** If your regulator can't maintain a low side pressure any lower than about 25 psi, then you will need a needle valve that is capable of adjusting very finely when presnted with relatively high pressure. The higher the pressure, the smaller the valve opening the smaller the changes in valve opening required to make small adjustments. a few more comments below. . . sh --- Heather J Gladney <hgladney@comcast.net> wrote: > A No-Shok needle valve follows the solenoid. Is this > sufficient as a > metering valve? > Today I put the Victor regulator on, with no further > equipment, to see > if it was working. It does bring the pressure down to > about 25-30 psi > but no lower. That alarmed me enought hat I have not > tried to put the > rest of the equipment on. From the regulator, the line > goes to a > solenoid (which goes into a Milwaukee pH meter) then to > the No-Shok > needle valve. > > It had a needle valve on it. The old setup was one of > those > locked-together pieces with a Milwaukee regulator to > solenoid to needle > valve into bubble-counter, the sort of setup commonly > sold on aquarium > websites. When the overfilled CO2 tank blew out that > regulator, and > then the overflow wouldn't reseat, after many adventures, > I got the > Victor. THe Milwaukee setup took some tweaking to get > the flow where I > wanted it, but once I got it set up it was fine. I ust > figure it'd be > nice to have a regulator that doesn't die when the > overflow valve gets hit. The rebuild kit for your medalist regulator is listed at $37 retail and probably is available for less. The "overflow" is basically a spring and disk and replaceable if it malfunctions. > I'd still like a bubble counter screwed inline like that, > but apparently > the Milwaukee setup uses some wierd French threading that > the gas store > guys had never seen before, and it'd be amusing trying to > get adapters. > The other buibble counters I've found have been the kind > you put into > the flexible airline, not into the needle valve > I haven't bothered to hunt down further, as part of the > tank diffusion > setup has one of those yeast-bottle bubble ladders, which > I figure will > give me a rough idea a little sooner than the pH meter. You can make a bubble counter out of pill bottle and some rigid airline tubing and some epoxy. The connect-to-airline-tubing ones work well. Bubble counters are a convenience and luxury, not necessary nor a good way to judge CO2 levels. All the less important ;if you have a pH controller and solenoid. Use pH, KH, CO2 table for judging CO2 levels. The Milwaukee pH controller, which it appears you are using, is very reliable. If you know your KH and desired CO2 level, you can set the Milwaukee and count on it to maintain the pH within 0.1 unit higher and 0.1 unit lower, which is the range for it's trigger points. > Thanks very much for your help! _______________________________________________ AGA-Member mailing list AGA-Member@thekrib.com http://lists.thekrib.com/mailman/listinfo/aga-member